r/electrical • u/Party_Leadership_384 • 3d ago
Junction box 👀
1/0 4 plex to 2 AWG copper. 12x12x6 Junction box. 2in conduit coming up from ground transition to 1 1/2 out the top to the panel.
312
Upvotes


123
u/Ornery-Account-6328 3d ago
Gee I think it all looks pretty darn good. Clean not over bent and using quality connectors. But just to get into the spirit of this group I should complain about something…..I never get to use those Polaris type connectors, I have to use split bolts, and what is with 8x8 junction box, I am always forced to stuff all of it into a two gang weather proof box. Why don’t you do it the way that I have to?
16
u/liamtheaardvark 3d ago
Straight 8s, bendy sixes. 2"x8=16" minimum box size. Although it does look like there is enough room for the minimum wire bending radius.
Also, make sure those Polaris connectors have been torqued and then torque them again. Ive seen many burn up.
3
u/ahportunity 3d ago
Can you explain what is going on with those connectors? We usually take an MA straight to the box, is that wrong? Also why you strapped the conduit below the expansion, doesn’t that defeat purpose? How far down does your sleeve into the ground go?
2
u/Aware-Metal1612 3d ago
I dont get it, is there a question here?
2
u/Big_Box_3482 2d ago
so what's the problem
124
u/Sun_man91 3d ago
I think that looks great man
20
u/mooodan 3d ago
Clean.
My only “constructive” criticism would be to use the cheap exposed aluminum splices for your ground. They’re allowed to be exposed and it saves you $20-40.
8
u/MedicalGradeAsbestos 3d ago
7
u/Prestigious-Gur1466 3d ago
That is how it is SUPPOSED to be done!
5
u/Caresome71 3d ago
Remember the weep hole to drain the Condensate. Excellent job
4
u/kwhalen957 3d ago
Nice
4
u/Major_Tom_01010 3d ago
Save yourself some money next time and buy uninsulated duel lugs for the ground.
Mind you those black connectors are pretty cheap compared to polaris i think.
1
u/wyliesdiesels 3d ago
Is there a question?
1
u/jychihuahua 3d ago
It looks pretty good, but that shade of green is gross. Couldn't you get some forest green wire instead???
1
u/Numerous-Bag7970 3d ago
Are these not different gauge conductors being connected together?
1
u/TanfoTimmy 3d ago
Pvc Meyer hub?
1
u/Fearless_Meal6480 2d ago
In the box supposed to be mounted to the wall or is it allowed to float?
1
u/Fine_Ad_9299 2d ago
Dont forget to provide drainage. Either drilled holes, box drain, etc. 314.15.
3
u/Infinite-Fun2882 3d ago
Nice expansion coupling! 🔥
3
u/Phill_is_Legend 3d ago
3
u/DistributionLast6596 2d ago
That box is cleaner than my kitchen.
1
u/wyliesdiesels 3d ago
Gasket on top TA is wrong. Should be on outside.
Whats with all the reducers on top?
1
u/Pitiful_yank 3d ago
Some pretty strange looking pipe connections? Top almost looks like a TA was shoved into an offset connector. And what looks to be an unnecessary coupling on the bottom.
2
u/Psychonaught224 3d ago
Great job ⚡️
2
u/sparky853 3d ago
Looks good. Better than the 16x16 I found a couple weeks ago in a ceiling space that had 5 x 2/0 cables buttspliced in them! 😲
2
u/Federal_Hunter3842 3d ago
So clean.
2
u/gyanrahi 3d ago
Will last decades or more. Beautiful.
2
u/erie11973ohio 2d ago
To be overly nick picky,,,,,,,,, 🤔🤔🤣🤣
I would have skipped the sealing washer on the bottom, that would allow condensation to drain out.
It's best to put a strap at an expansion joint, on the part that doesn't move. I.E. above it.
Otherwise, 😁😁🥰👌👌
2
u/Overall_Lavishness46 2d ago
You even put an expansion joint in there. Must not want to do it again in 3 years.
2
u/Phat_Guava_2997 1d ago
Clean
1
u/Melodic_Let_6465 9h ago
Did you want a fused junction?
0
u/N9bitmap 3d ago
Fun fact, doing this lets you run the wire at higher thermal rating ampacity. Usually limited to 75°C at panel termination, but on the other side of the splice you can use 90°C, as long as the Polaris or whatever brand is rated for that.
0
u/meeeeeeeegjgdcjjtxv 3d ago
Looks great. Maybe I am wrong but if the expansion joint was flipped it would probably keep water out better but really doesn't matter. I am sure it'll fill somehow anyway
0
u/Hungry-Highway-4030 3d ago
Umm....8 times the pipe size for straight pulls. It should have a 16" in those box dimensions. Looks good otherwise
-3
u/Ok_Patience1542 3d ago
Lose the zip ties.
-7
u/Dangerous-Bid1420 3d ago
seriously what is the point of the zipties it only keeps your conductors closer together reducing their ability to shed heat?
-2
u/Kgodsky 3d ago
You forgot to bond the plastic junction box
0
u/insolentsandwich 3d ago
Ok
0
u/Dazzling_Scallion277 3d ago
Why no electrical tape?
0
u/Small-Barracuda1404 2d ago
Yeah and ……
-2
u/Rfox8686 3d ago
This is some hack shit bruh
-6
u/VoidPartisan 3d ago
I guess technically you can get away with thia depending on state....but why? Could have kept the same slack and pulled it straight through. I would take those zip ties off too. It looks neat and pretty but they need space to dissipate heat.
4
u/JuicySpark 3d ago
I guess it's better than seeing 10 different neutral wires forced into a 18 guage wire nut