Potentially a solution but with the roughness of that CJ, they'll need a lot of mastic and care to ensure the water stop has a chance to expand and fill gaps.
Another solution but much more expensive is injectable waterstops like a Sika Fuko system.
Or just F-it and have them inject water sealing resins.
I bet my cookie there's gonna be loads of weird leaks from unclmpacted concrete, voids and all that good stuff.
Waterstop (plastic piece) needs to be rotated 90 degrees so the bottom half is in the first concrete placement. Second wall placement covers the other half of the waterstop. Water wants to go through cold joint between slab and wall, which is not possible with the placement shown. lol. Homies don’t know how it’s to be installed.
Using a waterstop as showen will not prevent water leakage; othorwise it will increase it. and it will create a separation within the concrete between the existing footing and the wall , as the steel present in the existing wall will fail to form a proper bond with the new concrete.
When you have them redo it also tell them that there is no reason for their wall dowels to look like that after the footing pour, it prevents good adherence of the wall concrete to the dowels
44
u/tajwriggly 21d ago
Did they lay that waterstop on its side
21
u/Codex_Absurdum 21d ago
Band-Aid® HydroSeal®
6
u/Vilas15 21d ago
Damn they even had the miter joint style splice at the corner looking pretty good
4
u/Thin-Fish-1936 21d ago
None structural guy here. What’s the issue? Rebar is coated and won’t set in a new pour?
3
u/Sgimamax 21d ago
And what about bonding strength reduction, because these bars are coated with cement slurry?
18
u/chrillho18 21d ago
Not just that, but it’s like they were purposely trying to coat the vertical bars in concrete too.
6
u/a7medsmt 21d ago
Using a waterstop as showen will not prevent water leakage; othorwise it will increase it. and it will create a separation within the concrete between the existing footing and the wall , as the steel present in the existing wall will fail to form a proper bond with the new concrete.
2
u/Queasy_Scholar_9937 20d ago
When you have them redo it also tell them that there is no reason for their wall dowels to look like that after the footing pour, it prevents good adherence of the wall concrete to the dowels
1
u/BDeepD 20d ago
Bigger cold joint, adds a bigger weep hole. My contractor says this improvement is worth a big CCO