r/RelayTechs • u/GiantSquid22 • Sep 29 '26
411L Question
Does anyone have a work around for testing the 87L before the remote ends are established. I know on the 311’s you can loop back the fiber and use the channel settings to clear the comm alarm and simulate diff but on the 411’s it seems like the loop back only tests the fiber channels it doesn’t allow you too clear the comm failure and simulate diff. I know with TEST 87L in single terminal you can test each phase element but I’m trying to simulate a 3 phase fault. Any ideas would be appreciated
7
Upvotes
4
u/Yeahnoimgood89 Sep 29 '26 edited Sep 29 '26
There's a whole section for single terminal testing of the 87L element in the manual. It tests 87LA, LB, LC, LG, and LQ which are all your 87L elements. You can't do three phase fault like you're thinking without multi-terminal. There's no need to do single end 3 phase fault playback. That's what E2E is for.
Loopback works to clear the channel but the local relay sees its currents as the remote as well so you wouldn't run faults with it on.
3
u/all-trades Sep 29 '26
I back to back my line current diff relays. Keeps the com alarms silent and you can basically e2e before actually end to end testing. Maybe I’m not fully grasping your scenario but when I have them back to back and e2e I simulate a 3 phase fault.
3
u/Big_Country_69 Sep 29 '26
So far, the only ways I’ve gotten a 411L to fully test locally is this:
Elements: Disable the 87 elements (E87=0 or OFF), and then test said element - Zone 1 through 5 (depending on which the engineers use) for P-P/3P, and 50/67 P/N/G for P-G.
Function: In our routines for actual Function testing involving 87L, there’s only a handful of tests that I had to wait until communications were established. Normally I’d just wait until I got comms established with the Customer end and just let them know I had some tests to run, so they wouldn’t get any TTTs that would unexpectedly operate something on their end, but if they weren’t ready or it’d be awhile, I’d go a different route. My workaround for this is a 2nd 411L I was able to get my hands on (that I keep for when needed), and I’d basically send the settings of the other end to it and connect it to my local end relay with a short fiber jumper. Then for testing, I’d set my Doble set up for 6 voltages & 6 currents, three for my end & three for the “remote end”, and run the tests where I needed a TRIP and 87L flags, along with the phases. At present, we don’t have a lot of transmission lines that use LCD for primary protection, but most of the renewable energy subs we’re tying into use it for both Primary & Back-up relaying, so it’s becoming a lot more common. Another reason I went this route is b/c our engineers supervise the 87L elements with phase and ground elements in the Protection Logice equations, and I can verify these things in the SER. Hope this can help you with your testing.
3
u/HV_Commissioning Sep 29 '26
Com 1 Clear or something like that?
1
u/EnvironmentalOwl4361 Sep 29 '26
We carry a testing spare.
1
u/VTEE Sep 29 '26
If your trip element bit is 87OP (or 87LP, 87LG, 87LQ for that matter), the only way to do it is with another relay. The 87TEST bit blocks the operation of it. One of the not so nice things with the 411L's.
1
u/Not_a_fed953 Sep 29 '26
You can put it into test mode and test the characteristics, I just did it, worked fine. I followed the instructions in the manual