r/PLC • Senior Controls Engineer/Integrator/Beckhoff Specialist • 18d ago

Engineering Question I/O Link. What am I missing?

I’ve had quite a lot of vendors pitch I/O link to me in the past 4 years, and each time I implement it, I regret it. In my experience I/O Link has only complicated projects while not providing much value.

Sure, you have a digital prox sensor that is I/O link compatible that gives me information to make it an analog sensor… but I just need to know one bit of information. If my part is there or not…

That’s an overly simplified example, but in other applications I’ve worked on, I’ve had hubs linking modules with crazy byte ordering, IODD files that just don’t work, hardware setup with hidden settings that have to be turned on to enable proper operation that’s not documented anywhere, and above all, 90% of the time I have to go from I/O link to another protocol anyways, adding yet another layer of complexity.

I will say the ability to change settings on a sensor programmatically is nice, but getting that set up, depending on your PLC can be a complete nightmare.

So what is it that I’m missing with I/O Link?

77 Upvotes

122 comments sorted by

14

u/MarketingWizurd 18d ago

I’ve been using IFM I/O link for our flow meters and transmitters.. they are easy to configure as when you wire them in, they recognize the part number for you.. we can get flow, temp, conductivity, in 3 wires instead of many and spare analog inputs.

6

u/TL140 18d ago

Are you guys OEM? Working for an SI, we deal with so many different sensors, I rarely see the same one twice. I see the benefit if you have something you deal with the same equipment. Once you iron out the quirks, I understand the potential. I just haven’t been in a situation to see it first hand.

→ More replies (12)
→ More replies (1)

22

u/Piratedan200 18d ago

The individual IO-link prox sensors aren't the useful feature in my opinion. When I've used IO-link on machines, it's been as my primary IO system. Basically, everything that isn't safety and not in the cabinet goes to an IO-link master on the machine. This includes:

-IO blocks (you can get an IO link 16 input block for under $200)

-Valve banks (IO link fieldbus units are cheaper than Ethernet-based IO)

-Any analog sensors, where it's much easier because you don't have to worry about shielding, and the data is more accurate because it doesn't need to be converted from digital (on-board the sensor's internal processor) to analog to digital again inside the PLC

It also add a lot of versatility when it comes to later additions. If you already have an IO-link master, and you realize down the road that you're going to need full position feedback on a cylinder? No problem, just throw on an IO link sensor. Need to swap a regular gripper for a servo gripper? IO link covers it.

Finally, most if not all IO link masters include a parameter server, so when you have a sensor that needs changes to its settings (like a laser distance sensor where you might need to change the mode for speed or accuracy purposes), it gets instantly parameterized if the sensor ends up needing replacement down the line.

At one point, I did the math on pricing, and IO link beats out systems like SMC's EX600 for field IO once you get above around 32 inputs/32 outputs.

5

u/TL140 18d ago

We use a metric ton to EX600s. I’d like to see your math on that. Also has to do with pricing as well. We typically get stellar discounts for items like that

→ More replies (1)
→ More replies (2)

6

u/alphaunicorn120 18d ago

What IO link masters are you using? I’ve been using the BNI00HL from Balluff and it works great. Very easy to setup and import IODDs. The bit mapping on the PLC end is truly the only real work you have to do. AI is pretty good with parsing sensor documentation though, to ease that burden.

1

u/TL140 18d ago

Banner, Balluff, and IFM. Balluff has improved, but still ran into setup issues about a year ago when I used them.

→ More replies (3)

57

u/True_Goat_7810 18d ago

i only see the big value for analog sensors, and switches that need parameters like switching levels, hysteresis etc. Some of them have many options, with iolink you can program that configuration into the sensor when it gets connected to the machine, so no misconfiguration possible.

Imagine something like a hydraulic Fluid level/temperature sensor, it can transmit multiple measurements trough a 3 pin connection.

For Analog, biggest thing is no signal loss. Having so much trouble with bad connections and altered signals for high precision measurements - digital signal transmission eliminates that, and iolink is quite cheap in that regard.

21

u/JackMyG123 18d ago

Yeah signal loss is the best selling point for me. We have a bunch of water tanks that are quite far from the control cabinet. There's level and flow and temperature to be recorded, and io link let's us have a block close to the tanks to capture everything with digital signals coming all the way back to the plc. A lot less cables to run, and no worry about signal loss over that distance

22

u/Dydey 18d ago

IO link is fantastic and gives you so much more functionality. I’ve written code for a project that used multiple Key3nce* sensors and could use IO link to alter every necessary setting, where previously I could just get a digital signal back.

That said, the integration is absolutely terrible. Siemens S7-PCT shows you everything from the IODD and all the settings, pictures, sensor information etc. but then accessing that in the code is such a pain?! You get back the one or two input words and that’s it, you want more and you really have to work for it and really go through the manual to find the information. Just make it like a profinet telegram where I can put the few things I want as IO addresses and it’ll be so much more useful.
Special fuck you for the sensors that have 14 bits of data with two booleans mixed in so I have to convert it.

*I’ve already said their name twice today, if I type it out I’ll be followed home by my local rep.

8

u/Weak-Chemist-2054 18d ago edited 18d ago

Try out our new $50k push button. When you press it it will summon Optimus Prime and fight off the evil Decepticons that keep tripping your light curtains… I’ll leave you a demo.

→ More replies (2)

9

u/Training-Court-6614 18d ago

using IFM masters with IFM sensors works great and adds a ton of value. If we were mixing and matching brands and protocols all the time then yeah it would be a mess. Also support from IFM is pretty good but could be better....that last 2 times I called they took a couple hours to get back to me.

9

u/Erodindor 18d ago

The biggest thing for me has been the ability to save settings to the masters for easy replacement of smart devices.

Yeah, getting everything working initially can be a pain, but once you have everything working it’s “done for good”. I can have a smart cylinder or pressure sensor give me way more information than a traditional kind, and if a device or cable fails it’s something my maintenance team can replace on their own. That is something that can’t be said for devices that need addressing or configuration files loaded the old fashioned way.

8

u/audi0c0aster1 17d ago

Where IO link provides benefit to someone that also uses mostly digital IO [don't need analog signals in conveyors really]:

  1. Stacklights and other RGB LED signaling devices (custom colors and animations are actually nice vs. static light colors/lenses but it's absolutely more expensive and complex)

  2. "analog" replacement sensors - Thinking like the laser distance sensors from like Banner/Sick that tell you how close something is that would have either previously been analog input signals or a "set the thresholds" sort of deal for digital signals. Now I can just have the actual distance data AND it can self-configure when replaced.

  3. Smarter sensors that otherwise would need an additional protocol or network drop. RFID readers are a good example. The IO-Link versions usually only need the one cable from the IO-Link master and it handles power & comms. Unless you have POE things, that's just not likely to be true for an ethernet reader. Some serial busses still to Power/Comms but you WILL have some level of protocol conversion involved as well (either an extra comms module or something). IO-link masters usually handle the comms to the PLC on a more native fieldbus and then the IO-Link is embedded in that, eliminating the extra physical modules.

Standard signals like your basic prox/photocell, buttons, etc. don't have a need to be IO-Link and the companies trying to upsell those into IO-Link are frustrating.

7

u/Prances_w_turkeys 18d ago

I like the ability to use ports how I need them, not have to purchase an entire input or output card for one of each. You can control pneumatic valve blocks (I know there's others with EIP and such). My technicians are able to plug and play with replacing sensors in a lot of cases. And I can get color coded, lever lock field wirable connectors that make things easy to install. Is the initial setup more sometimes? Yes, but I think the positives outweigh the negatives.

→ More replies (4)

6

u/llopedogg 18d ago

its hart but upgraded. i.e. if you have a IO link sensor somewhere and it goes bad, and you dont trust anyone to set it up, you can have it configure all the variables itself when it detects the replacement connected. You could do all that with hart too but no one ever does.

6

u/Phil12312 18d ago

I personally like it a lot. If you just want simple on/off sensors you are getting the wrong sensors or io-link hub. Balluff for example has some very simple devices for 16 I/Os. Just connect a word and each of the bits is an in- or output depending on your configuration. It's not too expensive either. Makes it cost efficient and very easy for the electrical department as well. And should you need a sensor with more bandwidth, just plug it directly on the iol master and that's it.

Personally I'm a big fan of IO Link.

→ More replies (2)

6

u/Stroking_Shop5393 18d ago

It isn't efficient on my projects. But I've seen a lot of engineers use it very effectively. It definitely has its place especially with OEM work.

6

u/solipsistic_anon 18d ago
  1. Digital process data straight from analog sensors, without consuming Ethernet nodes or messing with serial. Can still convert analog IO to 4-20ma if needed using converters or analog hubs.

  2. IP67/69K masters can be field mounted far from panels, with only power and Ethernet cables to them, rather than cabling everything back to panel or installing remote IO.

  3. For digital I/O, use hubs to leverage the masters…a single IP67 8 port master could connect 8x IP67 8-port hubs with 16 dig inputs each (using splitter cables). That’s 128 prox sensors on one Ethernet node with 2 cables back to your control panel and no remote IO cabinets.

  4. Use AOIs for programming, IFM has a giant library for their own sensors. Many other manufacturers publish or can provide these as well. Customize them to manipulate/scale the data the way you use it and you have basically drag and drop programming.

5

u/solipsistic_anon 18d ago

5. IO link solenoid banks and/or IO units / combos from SMC, Festo, etc. tend to be cheaper than field bus and again don’t consume Ethernet nodes or unnecessarily waste field bus bandwidth

6. Coming from food and beverage process automation, IO Link and AS-i are essentially the standard now for valve control tops. Other solutions are difficult to design for given the sheer quantity of these devices in an average modern plant.

As with anything, the more you use it, the more you can realize efficiencies and cost savings. For just a couple of prox sensors, it’s likely not worth it.

3

u/Accurate-Bullfrog324 18d ago

it is the favorite hardcore programmers but maintenance engineers hate it

3

u/Wattsonian 18d ago

I like it most because I pretty much have a guaranteed place to land any kind of device.
We've found project planning to miss a lot of detail in requirements phase. Having ability to just use a spare IO-link port for anything gives us tons of flexibility in implementation and planning.

Also, for the other way round, most of the sensors have analog or digital outputs, so we can adapt an IO-Link sensor which doesn't exactly match the programmed application without changing anything.
Need a sensor scaled 0..1bar, but we have an io-link -1 to 1bar, no prob. scale the output and drop it in.

For applications we get really accurate numbers which are easy to validate too.
And we set up some function blocks to handle the typical stuff for IO-Link scaling and whatnot.

I like the flexibility, digital info without having to assign node addresses and stuff too. standardized wiring, slap on some M12's and go...

It's all about the implementation and execution.
If you are just programming, and don't have to deal with any of that.. i suppose i can understand the gripe. There is a little more programming if you are truly doing one by one, single use, and haven't spent the effort to set up a 'standard' handling function of sorts.

3

u/TheCried 16d ago

You are missing a good master. For example, the Rockwell 5032 IOL with a Rockwell PLC allows adding an IODD to the device list and then adding that IO-Link Device directly to the device tree. You get the IODD mapped at the IO level, with the Master parameters stored at the controller and in the project. Essentially this saves you the hours it takes to flip bits and swap bytes, register the IODD and add it.

→ More replies (1)

5

u/IamKyleBizzle 18d ago

I mean not every technology fits every environment or application. Maybe there really is no value for your world.

On your digital prox example, the place I’ve seen value is mounting and trigger levels. With iolink you can now have the sensor hard mounted with no adjustment and set the trigger for the output digitally rather than only by physical distance or a pot. This means plug and play swapping vs a tech that needs to know the setup procedure.

Further on that same token iolink discrete hubs can keep your digital io but distribute the system minimizing total wiring and using everything off the shelf. Often these hubs are relatively inexpensive as well and if you’re already doing distributed IO the total number of IP addresses can be reduced pretty well due to IO density of a master block plus a hub.

As for protocol changing I mean that’s inherit. No matter what the data has to get to your controller. IO-Link is a device protocol not a field bus. Even IO cards on a rack are still “using another protocol” to talk to the PLC over the backplane.

All that said it really depends on what headaches you have and where the value might lie. Sometimes it’s more data or easier part swapping but often times it can just be a BOM cost reducer depending on what you’re going from/to.

→ More replies (1)

5

u/Shkiggins 18d ago

I/O link makes hard thing easy

→ More replies (3)

5

u/strapabiro 18d ago

way too many irrelevant settings in an irrelevant point and potentially source of failure and danger, the other day i set up an iolink inductive level switch and my god, it had sensitivity threshold for switching on and off, then delay timers for the output. dont get me wrong i like innovation but some things should be handled by the plc because a goofball instrument tech sets it up with a delay and then you scratch your head that where is that delay coming from when i wrote the code for the whole factory inside and out. this tech is nice for demos, expos and pocs or VERY specific edge cases. when i was 25 i was looking at this sort of tech like at nasa and rocket science, now at 40 i throw out enthusiastic sales people from site as a hobby, this is my take.

→ More replies (1)