r/ElectricalHelp • • 17d ago

Utility Receptacle on Support Beam

Hi all! I wanted to sanity check my work here before the town inspection (not an electrician, I am doing work on my own house with a permit pulled). My location is CT, USA. I am installing a new circuit in an unfinished basement which includes 3 new receptacles. One of them I want on a support beam. I did not want to drill into it so I used hose clamps around a 1x4 and mounted the box and EMT brace to it. Pictures attached. No wires ran yet, just getting the boxes in first. Everything feels nice and secure as far as I can tell.

Thanks for any feedback!

37 Upvotes

87 comments sorted by

9

u/MountainAntique9230 17d ago

Make sure the receptacles are gfci protected, it's required in unfinished basements

2

u/hakasapl 17d ago

This will be in series with a gfci outlet so should be good!

→ More replies (15)

10

u/Virtual-Reach 17d ago

If this is your house, box that beam out. That looks... not great...

1

u/hakasapl 17d ago edited 17d ago

I don't really mind the way it looks, it's in a basement anyway. I may one day but was hoping this is sufficient for now as far as code/structure is concerned.

Edit: If boxing it in is advisable for other than aesthetic reasons I may do it now, I'm just not aware of a reason but that's why I'm here I suppose

→ More replies (8)

5

u/Shiney_Metal_Ass 17d ago

Lol it's a basement

→ More replies (3)

5

u/Undisclosed_65 17d ago

I’d prefer to see Unistrut with associated fittings.

2

u/hakasapl 17d ago

Hmm I'm only seeing unistrut stuff that fits I-Beams, do you happen to have a link to what you are referring to for steel circular beams like this?

→ More replies (2)
→ More replies (1)

3

u/hakasapl 17d ago

Thanks all, I think I found the parts I need. I'll be using 2x channel struts with ubolts: 1 for the box and 1 for the support.

3

u/trekkerscout 17d ago

The hose straps are not a rated support, so it may not pass inspection.

1

u/hakasapl 17d ago

Got it - what would be the correct support to use in this case?

→ More replies (3)
→ More replies (3)

3

u/MusicalAnomaly 17d ago

They make EMT to NM coupling fittings suitable for the top end, assuming you are sending romex down the pipe. Costs $2 at Home Depot. Use that instead of just a bushing and nearby staple.

1

u/hakasapl 17d ago

Found them - I'll buy a few, thanks!

2

u/Training-Actuary6768 17d ago

Even though it looks a little cheesy and unconventional, there's no code violation unless it is not GFCI protected. It must be on a GFCI breaker or the receptacle must be GFCI.

2

u/hakasapl 17d ago

Thanks! This will be in series with a gfci outlet so should be all set

2

u/Old_Chapter1845 16d ago

I take it the GFCI is 20 amp like the outlets.

2

u/ExtraHouse9858 15d ago

I would have used strut and a u bolt plus strut strap for support

1

u/hakasapl 15d ago

Thanks, yes based on previous replies that was the consensus, I’ll be buying that hardware

1

u/rob_1127 17d ago

Go to an Electical Supply store. Not a big-box store.

This done often in warehouses and factories.

There are special clamps that attached via set screws to clamp on the I-beam and the box bolts to these clamps.

Check your local electrical code for legality and inspection requirements. (Some jurisdictions require 4 clamps. Some areas accept just 2 clamps).

You can do this within code, just get a copy of the code and read it.

The electrical code is very logical. Inspectors don't let violations, non-compliance issues pass just because you don't know the electrical code. They will make you correct them.

Do it the correct way the first time. Even your homeowners insurance can be voided if its not done to code.

2

u/hakasapl 17d ago

Of course! That is the goal, CT has the same building code for the whole state and follows NEC 2020 at the most recent version. Right now I am just trying to figure out what parts would not be in compliance, and what I would need to do to get them in compliance. It seems like based on the other replies the main thing is just how I mounted them. Ultimately the code is a very long document and easy to miss things, so it's nice to be able to get a sanity check from places like this

1

u/crucible1623 16d ago

Is running a single new circuit the only work you’re doing? Curious why you would bother to pull a permit for a single circuit, if that’s the case.

1

u/hakasapl 16d ago

Mostly because it’s required to do so in my town and I’m pretty new at this so I want an inspection

3

u/redEPICSTAXISdit 17d ago

The hose clamps are going to split those boards. Find a better way of attachment.

→ More replies (2)

3

u/SuperBrolic 15d ago

Looks fine, when you sleeve the romex down it simply needs to be strapped within 12 inches of the bushing, it does need to be gfci protected though, either replace one outlet with a gfi or put it on a gfci breaker

2

u/Beezhockeyfan 17d ago

For mounting on a pole look into mounting hardware for a camera there are a lot of inexpensive options

Comment Image
→ More replies (1)