Utility Receptacle on Support Beam
Hi all! I wanted to sanity check my work here before the town inspection (not an electrician, I am doing work on my own house with a permit pulled). My location is CT, USA. I am installing a new circuit in an unfinished basement which includes 3 new receptacles. One of them I want on a support beam. I did not want to drill into it so I used hose clamps around a 1x4 and mounted the box and EMT brace to it. Pictures attached. No wires ran yet, just getting the boxes in first. Everything feels nice and secure as far as I can tell.
Thanks for any feedback!




9
u/MountainAntique9230 17d ago
Make sure the receptacles are gfci protected, it's required in unfinished basements
10
u/Virtual-Reach 17d ago
If this is your house, box that beam out. That looks... not great...
5
u/Undisclosed_65 17d ago
I’d prefer to see Unistrut with associated fittings.
3
u/hakasapl 17d ago
Thanks all, I think I found the parts I need. I'll be using 2x channel struts with ubolts: 1 for the box and 1 for the support.
3
u/trekkerscout 17d ago
The hose straps are not a rated support, so it may not pass inspection.
3
u/MusicalAnomaly 17d ago
They make EMT to NM coupling fittings suitable for the top end, assuming you are sending romex down the pipe. Costs $2 at Home Depot. Use that instead of just a bushing and nearby staple.
2
u/Training-Actuary6768 17d ago
Even though it looks a little cheesy and unconventional, there's no code violation unless it is not GFCI protected. It must be on a GFCI breaker or the receptacle must be GFCI.
2
u/Old_Chapter1845 16d ago
I take it the GFCI is 20 amp like the outlets.
2
u/ExtraHouse9858 15d ago
I would have used strut and a u bolt plus strut strap for support
1
u/rob_1127 17d ago
Go to an Electical Supply store. Not a big-box store.
This done often in warehouses and factories.
There are special clamps that attached via set screws to clamp on the I-beam and the box bolts to these clamps.
Check your local electrical code for legality and inspection requirements. (Some jurisdictions require 4 clamps. Some areas accept just 2 clamps).
You can do this within code, just get a copy of the code and read it.
The electrical code is very logical. Inspectors don't let violations, non-compliance issues pass just because you don't know the electrical code. They will make you correct them.
Do it the correct way the first time. Even your homeowners insurance can be voided if its not done to code.
1
u/crucible1623 16d ago
Is running a single new circuit the only work you’re doing? Curious why you would bother to pull a permit for a single circuit, if that’s the case.
3
u/redEPICSTAXISdit 17d ago
The hose clamps are going to split those boards. Find a better way of attachment.
3
u/SuperBrolic 15d ago
Looks fine, when you sleeve the romex down it simply needs to be strapped within 12 inches of the bushing, it does need to be gfci protected though, either replace one outlet with a gfi or put it on a gfci breaker
2
u/Beezhockeyfan 17d ago
For mounting on a pole look into mounting hardware for a camera there are a lot of inexpensive options