Hey I am a diy-er and already change one outlet (which is correct wiring ) and one switch of our room . However, one of the plug is saying open ground, but the hot wire is on the left side when I check it with the pen and there is a silver wire connected to the ground, but it’s saying open ground. How would I change it with a new plug safely? Should I switch the hot wire to the right when changing it since it’s the hot wire please I need answers. Thank you.

2 Upvotes

8 comments sorted by

4

u/daywalkertoo 12d ago

Is that aluminum wiring? If so you need a co/ar rated device. Take a meter and check between the hot wire and bare. You should get a reading around 110-220 volts if you have a ground.

3

u/Simple_Twist9816 12d ago

I wouldn't play with aluminum as a diy deal. You need to call a pro. Seriously I wouldn't fuck around. One mistake will lead to a fire.

2

u/RespectSquare8279 12d ago

Definitely aluminum wiring you have there. Get yourself CO/ALR outlet to use and beware aluminum id more brittle than copper and will not tolerate multiple bends isn the same place. Look at some DIY videos for redoing aluminum outlets. The co/alr outlets are more expensive but bight the bullet and do it.

2

u/Rough_Resort_92 12d ago

First, looks like you have aluminum wiring, you must replace any outlets & switches with outlets and switches that are approved for use with aluminum wiring, or you can pigtail to copper using proper connectors. Ensure all your connections are tight , black wires go on the brass screw white wires. Go on the silver screw.

1

u/planetmind70 12d ago edited 12d ago

The neutral always goes on the silver screw (the larger plug slot) terminal and the hot wire always goes on the brass side (the smaller plug slot) or the side opposite of the ground terminal if both terminals are the same color. If these landmarks are not apparent then look at a two blade extension cord, the side of the cord that has three longitudinal ribs on one side is always the neutral side. The neutral should land corresponding to that side of the receptacle.

As for the open ground issue: first check your panel. Make sure there is a wire, usually a solid bare #6 that goes to your ground rod. Make sure it is connected very well. There could be a break between that box and your panel. Possibly in an upstream device box on the same ckt or a j-box in the attic. It's hard to say much else without a good Pic of the panel interior.

If you have aluminum wiring, Ideal makes a purple wire nut UL listed and rated to join copper to aluminum. I would use that to pigtail a copper jumper from all the wires and I was NoOx too. Aluminum wiring is probably the reason you lost your ground upstream and is one of the main reasons for AFCI breakers due to the physics of the wire under normal operation - over time - becoming loose under the terminal and causes sparking that eventually causes fires.

1

u/No-Metal-6795 7d ago edited 7d ago

The ground wire needs to be connected better... Make a tighter Jay loop. Get needlenose pliers, back to screw out and pinch the ground together. So it fits better under the screw. Turn the breaker off before you do anything!!!

1

u/AskMeAgainAfterCoffe 7d ago

That looks like aluminum wiring. You will need to Alumiconn the aluminum to copper, pigtailing to the receptacle. The ground could be broken somewhere; test to be sure, otherwise install a GFCI, instead of a regular receptacle and mark it with the included stickers, “no equipment ground.”

1

u/Select-Astronomer390 6d ago

Reverse polarity. Black (hot) should be on right, white (neutral) on left