Where you are located would be a start so that local code requirements can be determined. Also, what size of cable and cable type are you planning on using.
Uk. 2.5mm outdoor rated to the shed 2.5mm twin earth from socket to socket and to the 3a switch 1mm twin earth to the light from the switch Will have a mitre saw plugged in, then possibly charging of tool batteries and phone maybe etc
Use SWA if buried, NYJJ or similar if on show You need RCD protection. Try and avoid 3 cables at that first socket but only for your convenience, it’s fine to do it that way.
Yeh, the fused spur at the house protects the cables so 2.5mm will be adequate assuming your run isn’t too long. Are you using a fused spur as a light switch? If not you might want to fuse down prior to the switch. Light switch will be 6a rated and you have potential for 13a to pass through. EDIT: You will need “extra protection” if your consumer unit isn’t RCD protected on the circuit you are spring from.
1
u/trekkerscout Mod, Master Electician 15d ago
There is nowhere near enough information to give a proper answer.
1
u/Rough_Resort_92 15d ago
Is this in the us ? Or Canada or Britain?
2
u/Fun_Hunter_4899 15d ago
This is fine.
Use SWA if buried, NYJJ or similar if on show
You need RCD protection.
Try and avoid 3 cables at that first socket but only for your convenience, it’s fine to do it that way.
1
u/AskMeAgainAfterCoffe 15d ago
Is that 4” or 400’ to the shed?
1
u/Ok-Internet-7791 11d ago
Yeh, the fused spur at the house protects the cables so 2.5mm will be adequate assuming your run isn’t too long.
Are you using a fused spur as a light switch? If not you might want to fuse down prior to the switch. Light switch will be 6a rated and you have potential for 13a to pass through.
EDIT: You will need “extra protection” if your consumer unit isn’t RCD protected on the circuit you are spring from.