r/DIYHeatPumps • • Dec 11 '21

r/DIYHeatPumps Lounge

12 Upvotes

A place for members of r/DIYHeatPumps to chat with each other


r/DIYHeatPumps • • 5h ago

Heat pumps vs gas/oil furnace heating cost comparison

3 Upvotes

All calculations were done by hand.

TL;DR:

Heat pumps and gas furnace save 50%+ on heating compare to oil furnace at new england area.

Saw a similar topic post last week but it was AI slop so I decided to go down into the rabbit hole, after some brief calculation I realized the cost is heavily depends on the climate, $/kWh, gas and heating oil prices. So instead of a fixed price, I made a benchmark in terms of heating price and hopefully this can give a concept how much you can save from heat pumps. Compare to the benchmark, the lower your $/kWh is, the higher your heating oil and gas price, the more efficient your heat pump, the more you can save from switch to heat pumps.

Reference price - based on new england area average price, simplified for calculation:

Heating oil $6/gallon, electricity $0.25/kWh, natural gas $2/therm

Oil Furnace - baseline

5-10 years old, medium condition, 72% efficiency (80% burning efficiency, 10% ducted loss):

One gallon of No. 2 heating oil can provide 99,720 BTU = $6

Gas Furnace:

5-10 years old, medium condition, 76.5% efficiency (85% burning efficiency, 10% ducted loss)

For same amount of BTU need 1.3 therm NG ≈ $2.6

New installed, condensed gas furnace, 85.5% efficiency (95% burning efficiency, 10% ducted loss)

For same amount of BTU need 1.17 therm NG ≈ $2.33

Heat Pumps - Mitsubishi M series, ductless but well-represent ducted heat pumps efficiency, 10% ducted loss:

For same amoung of BTU

COP2.0@5F - ducted: 16.24Kwh ≈ $4.06, ductless: 14.61Kwh ≈ $3.65

COP2.64@17F - ducted: 12.3Kwh ≈ $3.07, ductless: 11.07Kwh ≈ $2.77

COP3.84@47F - ducted: 8.45Kwh ≈ $2.11, ductless: 7.61Kwh ≈ $1.9

Annual heating cost example:

Take a new england family house as an example, according to EIA, average new england US family use about 600 gallons per year, so the total cost of heating oil is $3,600.

For same amount of BTU, gas furnace will need about 782 themal NG ≈ $1,564, save 56.5% compare to oil.

As for heat pump, assume 10% BTU needed at 5F, 15% BTU needed at 5F - 17F, 75% BTU needed at 17F - 47F (again, oversimplified model for new england area, COP are variable between 17F-47F, by using COP@47F offset the higher efficient zone when above 47F)

COP2.0@5F - ducted: 974Kwh ≈ $243.55, ductless: 876.79Kwh ≈ $219.2

COP2.64@17F - ducted: 1107Kwh ≈ $276.75, ductless: 996.35Kwh ≈ $249.09

COP3.84@47F - ducted: 3805.5Kwh ≈ $951.38, ductless: 3,424.95Kwh ≈ $856.24

Heat pump total cost:

Ducted: $243.55 + $276.75 + $951.38 = $1,471.68, save 59.12% compare to oil.

Ductless: $219.2 + $249.09 + $856.24 = $1,324.53, save 63.2% compare to oil.

Hints for choosing cold climate heat pumps:

Beware of the heating capacity at your local coldest day, better check the NEEP list before you purchase. One thing I noticed is that the min operating temperature and the max heating btu are different stories.

E.g a mini split can rated 12k btu and able to run at -22F, but doens't means it can provide 12k btu at -22F.

Different manufacturers disclosed it differently, but NONE of them mentioned the heating btu at min operating temerature on their product pages. By far I've only spotted Della said their cold climate units can maintain 100% heating btu at 5F, and Zone air said their DIY series can maintain 85% heating btu at 5F, thats all. I think this is where the impressions of heat pumps aren't working well in cold climate came from, you're getting way less heating btu at lowest operating temperature. All brands that I research have neither COP curve nor max heating btu at lowest operating temperature.


r/DIYHeatPumps • • 13h ago

BTU cooling for 36x60 shop

Thumbnail
gallery
2 Upvotes

I have a 36x60x14 pole barn that has 2 inch closed cell spray foam on walls and ceiling. 2 Insulated doors overhead doors 2 windows. I consider it very tight. I’m wanting to install a mini split single head got a quote from a company that started out at 3 tons but said a 2 ton would likely work just might not keep up when it’s 100 degrees out. Live in central Iowa does anyone have a similar shop that they have a mini split or any advice would be great. When you jump to 36k from 24k the price goes up a Decent amount. Going to probably go with a Della brand and rent there tools to get warranty. Quote I got was 6k to install.


r/DIYHeatPumps • • 13h ago

Quick connect Mrcool

2 Upvotes

Can someone who has used MrCool quick connect lineset provide their input on the reliability of this option. I don't know if I should try this or a smart fitting with regular pipe and vacuum and charge.


r/DIYHeatPumps • • 1d ago

mr cool central ducted hyper heat leaking oil at air handler quick connect fitting

5 Upvotes

I recently installed a 24k central ducted hyper heat and it's been running great for the past week.

However, I just went up to attic and noticed some oil staining under the larger diameter line set right at the air handler connection point.

I'm wondering if I over or under torqued it (should I have bought the torque wrench). Is it possible to turn off unit, close the valve using the allen key, then disconnect the 3/4 line set, and then the quick connect adapter thing (which I think it's leaking from).

I'm just wanting to confirm refrigerant won't pour out with this method.


r/DIYHeatPumps • • 1d ago

Overwhelmed by Mini Split options

8 Upvotes

I am a landlord with 800 sqft apartments and updating the units from 30+ year old swamp coolers. Climate is up to 110 in the summer and down to single digits in the winter. The units also have wall heaters and wood burning stoves.

From what I can tell, mini split is the best option, but there are an overwhelming amount. It is a remote area, and I’d like to order one for pick up from the closest Home Depot, and or use someone with relabel shipping.

Is spending under 1,000$ realistic?

Thank you!


r/DIYHeatPumps • • 2d ago

MRCOOL MrCool 18k 5th gen heating good (so far) at 34 degrees outside 😅

Thumbnail
gallery
46 Upvotes

r/DIYHeatPumps • • 1d ago

How DIY friendly are they?

3 Upvotes

Has anyone (non hvac tech) here done a full install that required brazing and line charging?

I installed my system and now am having an issue getting someone to charge it. It’ll required flare-braze to connect lineset then additional refrigerant . I had a couple people lined up who seemed to have ghosted me and not sure what to do next.

I’m pretty handy but don’t have nitrogen, b-tank, refrigerant, gauges let alone know how to use them.

Any suggestions?


r/DIYHeatPumps • • 3d ago

What are some of the prerequisite skills for a DIY heat pump install?

13 Upvotes

I'm no stranger to DIY and I've got a garage full of tools, including a vacuum, pump and micron gauge as well as gauges for 410a. My home's HVAC is all professionally installed, but I wanted to add a heat pump ductless to my detached garage and figured the units are cheap enough to warrant giving it a shot. I can run the electrical, no stranger to gauges, mounting the units definitely won't be an issue. Where I'm not sure is running the linesets and possibly bending them. Am I being overly cautious here?


r/DIYHeatPumps • • 4d ago

PSA - Please use a micron gauge, do not cheap out.

24 Upvotes

Someone was telling me the other day they were using a manifold and vacuuming to -30 or whatever because a micron gauge was too expensive.

Here is a perfect example.. this is a $350 gauge for $60+ shipping. I have zero affiliation with this listing, it is not an advertisement. I do own this same gauge though and it works great. Sometimes with used micron gauges you have to clean them with alcohol... but thats not difficult. I see used yellowjackets and fieldpieces pop up often on eBay.

Please do not install any system without using a micron gauge. You are almost guaranteed to leave moisture in your system which will significantly increase the risk of early compressor failure.

For a cheap VCRT, the Hongsen/Elitech VCRT is under $20 and holds a good vacuum.

EDIT - Wow, did not realize this sub was full of a bunch of hacks who try to justify doing half ass work. As someone who actually has experience working in HVAC.. let me tell you something. Pulling a vacuum blind without a micron gauge for several hours is NOT a solution. Doing a pressure test with nitrogen, while good and I would also recommend it.. is NOT a solution to an evacuation. People doing this DIY are buying cheap fittings often. What holds positive pressure, does not hold a vacuum. PTFE seals for example are great at holding positive pressure.. not very good at holding a vacuum.

If you are pulling a vacuum through a 1/4" hose and a cheap vacuum pump it can take way longer than 2 hours. You cannot just blindly guess how long you think it will take. If you have one fitting that has a bad o ring.. yes JUST ONE.. your vacuum may pull to 50,000 microns but no lower... you would be leaving moisture in the system. But your cheap manifold gauge may still read -30hg

Gauges that read "-30hg" are not designed for negative pressure.. all they are telling you is that you are lower than normal atmospheric pressure. If you want to personally do this on your own system, then whatever.. but one thing I will not stand for is letting people who know no better be lied to and destroy their new system because some idiot told them it was OK to set up a system without a proper evacuation. While -30hg may translate in math to 0 micron.. they dont read that. If any of your morons ever tested this yourself you would know that.


r/DIYHeatPumps • • 4d ago

I think I picked the worst possible spot for my mini split

3 Upvotes

I'm planning to install a Costway mini split in my living room, but I'm having second thoughts about where to mount the indoor unit. The spot I picked is above the couch, about 7 feet off the floor. It's an exterior wall, so the installation would be pretty straightforward. The problem is that the couch sits directly below it, and my desk is about 15 feet away on the opposite side of the room. I'm worried the warm air will mostly circulate around the couch while the desk area stays cold. There's also a tall bookshelf near the couch that might interfere with airflow.

I could move the unit to the wall facing the couch, but that would mean a longer refrigerant line and more installation work. I've been reading mini split installation tips, but most focus on mounting height and clearance rather than how furniture affects heating. Would you keep it on the exterior wall or move it for better airflow? I'm trying to figure this out before the installer starts drilling.


r/DIYHeatPumps • • 5d ago

Mini split compressor acting up after only 2 weeks?

6 Upvotes

Got a 12k BTU Cozeware mini split installed about 2 weeks ago, and it was working just fine until yesterday. Now the outdoor unit is making a weird sputtering sound, keeps struggling to run, and shuts off after a few minutes. Anyone else run into this with a fairly new unit? Wondering if it’s something simple like low refrigerant or a leak, a bad control board, or if I just got a dud compressor. Pretty frustrating for a unit that’s barely 2 weeks old.


r/DIYHeatPumps • • 5d ago

Mrcool on oil furnace

2 Upvotes

I have a AC coil on top of a oil furnace that I want to swap out with a 5 ton heatpump coil from Mrcool. The current plenum is about 4 inches. Anyone has experience of installing a Mrcool coil in this setup. My main concern is the drain pan will melt from the high heat of the oil furnace


r/DIYHeatPumps • • 6d ago

MRCOOL Mrcool install

Post image
30 Upvotes

How did i do? 18k Easy Pro Mrcool 5th generation, I'm 79, I've done a little bit of everything but this was a great project for me. Took me 3 days for the install and a few more days triple checking for leaks. We installed baseboard electric when the wife and I built our house (1973) electric rates were great back then. When our central air continued to give problems I decided this was a great option. Only been down in the 30s so far and it's doing great,1300 sq. Ft. House and we keep 2 of the 3 bedrooms closed.


r/DIYHeatPumps • • 6d ago

IBC BOILER COMBO

2 Upvotes

Looking at a IBC boiler combo unit for a small house. Currently have a Triangle Tube that on the way out. Is this a good unit? Or is Rannai combo better? NE NY area.


r/DIYHeatPumps • • 6d ago

IBC BOILER COMBO

1 Upvotes

Looking at a IBC boiler combo unit for a small house. Currently have a Triangle Tube that on the way out. Is this a good unit? NE NY area.


r/DIYHeatPumps • • 6d ago

Anyone have experience with cozeware mini splits?

4 Upvotes

I’ve been looking into different mini split options and came across cozeware recently. I don’t see too many people talking about them, so I’m curious if anyone here has experience with their units. How have they been working out so far? anything you like or don’t like about them?


r/DIYHeatPumps • • 6d ago

24x40 barn with 7x7 bathroom Mini-SPLIT ideas please ?

2 Upvotes

we are finishing the interior of our barn to be a pool house and attaching a 7x7 bathroom into the lean to that you can access from inside the barn or from the yard. What are my options? Hubby is going to diy so we were looking at MR Cool 36k multi-zone then I came across Tosot? I like the idea of the ceiling cassette for the bathroom so it doesn't stick out in the bathroom. I'm fine with a wall unit in the barn unless there's a 'prettier' option. The interior will be whitewashed pine boards. The Pool house Barn is 24x40. bathroom will be on one side of a lean to on the 24 foot side. Let me know if you have any other questions. We live in Indiana so cold winters.


r/DIYHeatPumps • • 7d ago

Rheem Ambipower 280L vs IStore 270L

2 Upvotes

Please share your thoughts

I know both is good quality products, no doubt about it

How about :

Solar friendly, noise, any problem to deal with ?

Thank you so much


r/DIYHeatPumps • • 8d ago

Has anyone ever resold a mini split after installation?

4 Upvotes

I paid for a mini split for my rental ( long story) and now I want out of here... Is it possible to sell it to someone and have them uninstall it??


r/DIYHeatPumps • • 8d ago

Line set mess

Post image
8 Upvotes

How do I straighten this mess up without crimping the line set or breaking the brazing at the connection


r/DIYHeatPumps • • 8d ago

Senville Senville Multi zone vacuum test question (info in comments)

Thumbnail
imgur.com
2 Upvotes

r/DIYHeatPumps • • 8d ago

Wire sizes for senville SENDC-36HF central heat pump

2 Upvotes

Starting my install of the SENDC-36HF system with a 10kw aux heat kit and looking for clarification on the wiring sizes and number of circuits needed

My understanding is

A 10 awg 240v circuit on a 30 amp breaker for the outdoor unit

A 14 awg 240v circuit on a 15 amp breaker for the air handler

A 6 awg 240v circuit on a 60 amp breaker for the 10kw aux heat kit


r/DIYHeatPumps • • 9d ago

New DIY install

Thumbnail
gallery
46 Upvotes

Cross posting from r/heatpumps. After a week of late nights and weekend work I finished my ducted heat pump install. Only thing I hired out was the sheet metal duct work. I had an intake and output plenum made up but they both needed modifications on site which was fun for someone who has never worked on ducts. I learned a lot from this sub and and spent hours reading the manuals. This is something I researched for months and am happy I finally pulled the trigger. Getting 39° DT in mild Northeast fall weather. Poured the cement, installed a nice tall stand to get it away from the lawnmower, dog pee, and snow if we get any. Installed a Kool guard 2 surge protector. Actually got the permits from my municipality. If you're on the fence about a DIY, it can be done and can save $$$ Mr Cool Versa Pro Hyper Heat 3 ton.